As title - I’d expected system to be fully independent in the event of a power cut, but when I turn off the main DNO isolator to test system behaviour in the event of a power cut, AIO kicks in perfectly, but PV generation is shut off - regardless of SoC of AIO?
Is that expected behaviour? Appreciate there can’t be any export from the system in island mode, but I did still expect the solar to function?
Please elaborate - is your PV being fed into your system as DC or has it gone through an inverter already (as per many FIT systems) and being fed as AC into the Gateway?
Also when you state PV is ‘shut-off’ - how are you monitoring this? Via the App?
Could it be that the PV is being directed to your house consumption (along with the AIO output) rather than being used to charge the AIO?
PV passes through a Solis inverter in the loft before entering GE equipment.
When I turn off the main DNO isolator, the separate PV meter turns off and no PV is reported either in the GE app or passing through the PV meter on the Gateway.
A Solis inverter will go offline if it loses power because it is designed to disconnect from the grid when there is a power outage, as this is a safety feature to protect the grid from potential backfeed issues; essentially, it stops producing electricity when the grid power is absent, meaning it goes offline until power is restored.
Aye, I’d expect the Solis inverter to go off line if there wasn’t the AIO & gateway present during a power cut, but wouldn’t the AIO should takeover replicating the Grid supply when in EPS mode and gateway in island mode should prevent any export back to the Grid?
Or am I misinterpreting / misunderstanding the expected behaviour?
Aye, but I don’t have access to the logs - Solis data collector wasn’t installed, will see if I can get one from the installers so I can access the inverter.
Definitely one for your installer to look at initially. Hopefully they installed an earth rod, as that’s a pre-requisite for an AIO if you want to continue generating PV.
There have been lots of issues with this in the past, both from the installer side with not installing earth properly / at all, to the Gateway having issues with off-grid mode.
When all working properly, the Gateway effectively tricks the inverter into thinking all is still well with the grid, which is what allows PV generation to continue. If the inverter detects anything is amiss then it will shut itself down until it sees the grid being back online.
Yes, definitely have an earth spike - well, at least they ran the cable and installed the ducting for it - I’m assuming it’s actually connected in the ground
Hi,
Its probably to do with your solar inverter, i know when you use growatt inverters you have to get growatt to remote into your inverter and change a setting to do with grid monitoring. On grid mains will have slightly different characteristics to off grid mains and might be tricking your inverter into thinking its lost mains. It might be worth getting your installer to ring givenergy as i know they are aware of these issues, or ring solis.
Phil
I would expect the PV to go off, until the SOC has dropped sufficiently for the PV to go somewhere. If you are disconnected from the grid, unless the PV can fully be consumed by the house load and/or battery charge then it would need to be disconnected until it can