Charge rate maxes out at 5.7kW and constant low Export to Grid?

Hi there,

I had my AIO installed a few days ago and have been monitoring it and have a few queries.

Firstly, it charges at a rate of 5.7kW max when it should be 6kW. Are there any reasons for this and things I should look into?

Secondly, the portal reports a steady low export to the Grid (<100W) when the battery is 100% powering the home. Is this expected or is there a setting somewhere to turn this off? My expectation is that this should be Idle when the battery is powering the home.

Thanks for any input in advance.
Ben

What version firmware are you running ?

You might just need a update

I am on Inverter Firmware Version D0.611-A0.611.

It was only installed 2 days ago so sure it will be on the latest and greatest?

Re charging at 5.7kW,

  1. It’s possible that your main incoming voltage is a bit low (ie below 230v)
    5,700w / 26A = 219v
    6,000w / 26A = 230v

  2. Has a charge rate limit been applied in settings?

1 Like